I don't pretend to be a VFD expert but I'm hoping someone has some insight. I have a VFD in this facility on a newer system installed 3ish years ago before I was employed on site. Unfortunately when they bought this water system they didn't have the manufacturer commission the equipment so some of it didn't get tested after the install. Long story short - This drive and pump has never been online. Working with the engineers to try and get the pump going, I manually power up the pump off the VFD, the drive shoots to 40A, then eventually faults. I took an amp reading on the VFD output (while the readout said it was pushing 40A) and each phase is reading less than 2A. I've taken the motor out, meggered it, check for locked rotor and everything checks out fine. Plus I switched leads in the enclosure to a VFD I know is functioning and the motor spun up just fine. Is there a setting somewhere on the drive that I'm missing? Or is the drive just faulty? Again, the drive has 0 hours on it so it's odd it would have failed but I've seen stranger things.