Presuming the meter is reading correctly, high usage or an increase in cost per kWh, but that could be caused by one of several electrical issues.I have a customer who is complaining of an abnormally High electric bill is there any type of issues that would cause this or could it only be caused by high usage
$s or KW?I have found issues where a direct bury electrical line was damaged and the power was just dumping to the actual ground.
One customer had a trailer and between the pedestal and the trailer was direct bury USE wire. An animal chewed through one of the lines, and the power bill went from 200 ish a month to 8500 a month.
Frozen condenser is really bad, frozen evaporator is more common thoughwell pump short cycling
AC condenser frozen
broken ductwork
any kind of water leak if on a well
I had one that was easy to find, locked down motor (don't remember but I think was AC) repeatedly trying to start, kick out thermal overload, after overload cooled off tried to start again
Unless you find something obvious, you really need to see bills, both the "usual" and the "high" bills. Anything on that bill that raises the $$ but isn't a direct result of usage and you will be searching for something that doesn't exist.I'm going out tomorrow to investigate the house has gas heat and hot water and window units as far as the kw usage I'm not sure I would have to see the Bill
Sent from my SM-G950U using Tapatalk
To add to that, budget billing with any utility usually is reviewed annually and re adjusted. If one thinks their bill can't go up and is careless with usage, it will go up. You not only have to make up the difference at the end of previous year but the base for next years estimated usage is likely going up as well. Some may screen the budget figures at six months to see if you are on right track and make adjustments then if you are not so you don't end up with a huge difference at the end of the year.Also check to see if they just had an anniversary for their Budget Billing. I've seen annual bills spike because some people believe once they're on the Plan, their bill cannot go up. Yeah, it can.... if you use far more KwH than predicted.
Sorry but I can't see the water heater element failure driving electric usage up. Still is dependent on how much hot water is used. With the typical two element units, failure of bottom element just means you are not heating the lower portion of the tank, top portion of tank will still shut off upper element when it reaches it's setpoint. If anything your energy consumption maybe lessens a little because you are not heating the lower portion of the tank. It takes X amount of watt-hours to raise Y gallons of water Z degrees whether it is done by one element, two elements or even different sized elements.A few things we have found over the years that will drive usage high:
1) As previously mentioned, bad insulation on direct-buried service cable - even if the drop is overhead, they may still have underground service to a garage, shed or swimming pool
2) Loose connections in main service panel - although this will usually result in intermittent outages or severe flicker events - we usually just check for abnormally hot breakers
3) Bad jaws in a meter socket - although, as in the above, there will usually be intermittent outages or severe flicker events
4) Heating strips that the homeowner is unaware of (small ponds, garages, outbuildings, etc) - if thermostat goes bad and they remain on, it can put a real whammy on the usage
5) Dual element water heater with bad primary element - if the tank is large enough, the secondary element never shuts off
Probably many more, but that's just off the top of my head![]()
There had to be more going on there then just losing the bottom element, and presuming nobody modified how they are connected from the factory. Once water in top of tank reaches the upper thermostat setting it transfers to the lower element. If it isn't working, upper element will come back on again after top of tank is cool enough to switch upper thermostat again. If lower element is working properly, top may never come on again if hot water draw is never more than what lower element can keep up with maintaining at the top of the tank.unfortunately, I not only can see it but in early nineties with Dominion Resources had it happen. Water heater lost an element and second element just kept chugging... water was real hot, but we just thought that was ok, as it had been that way since we bought house, what did we know... actually thought someone was stealing our power because bill one was 600 bucks.. this was 1990, mind you.. we made double sure what was left on, unplugged stuff, etc... second month, 650 bill... started unplugging everything... third month, 600 bill... we are really struggling to cover things as also new baby in house as well...lol... diapers, maternity bill... boom... panel breaker blows to water heater... flip it on, blows again.. call my buddy.. he shows up, checks stuff, asks how the water heater had been doing..we told him we had set the thermostat to low but it was still too hot... he was laughing...
he replaced the thermostats and the heating elements... cleaned everything up.. took my money and some rum..and my next bill came in.. 375... next month, with christmas lights and extra heater, bill was 145... bill dropped to an average of 118 dollars a month after that...lol...