This can be kind of confusing so just bear with me. I encounterd a power issue on a UPS supplied transformer. To not make this overly long I will try and sum it up. Metering at the main breaker of the panel, these are the voltages that I found:
3P-4W 120-208 system
A-phase to Ground-0v
B-phase to ground-210v
C-phast to ground-210v
Neutral to ground-120v
a-b 208v
a-c 208v
b-c 208v
The line side of the transformer reads 480 accross the board and everything is correct voltage wise there.
I had an outlet that stopped working and thats when i noticed the strange voltages and went back to the main at the panel. Just to verify I made sure I tested with a second meter and everything came out about the same. This was yesterday, today the voltages seem to be fluxuating almost like a lose connection point somewhere. In order to get the outlet working again and to be able to get 120v from phase-neutral I had to disconnect the ground wire at the device.
I guess my question is does anyone out there think this could be a ground/bonding issue at the load side of the transformer or could this problem actually be caused by the transformer itself. It seems to be localized to the panels feed from the load side of the transformer. I tested other outlets and equipment from the panel and it seems like this doesnt happen on anything feed from b or c phase but only on a phase. I am kinda scratching my head at the moment and Any insite would be appriciated.
thanks!
3P-4W 120-208 system
A-phase to Ground-0v
B-phase to ground-210v
C-phast to ground-210v
Neutral to ground-120v
a-b 208v
a-c 208v
b-c 208v
The line side of the transformer reads 480 accross the board and everything is correct voltage wise there.
I had an outlet that stopped working and thats when i noticed the strange voltages and went back to the main at the panel. Just to verify I made sure I tested with a second meter and everything came out about the same. This was yesterday, today the voltages seem to be fluxuating almost like a lose connection point somewhere. In order to get the outlet working again and to be able to get 120v from phase-neutral I had to disconnect the ground wire at the device.
I guess my question is does anyone out there think this could be a ground/bonding issue at the load side of the transformer or could this problem actually be caused by the transformer itself. It seems to be localized to the panels feed from the load side of the transformer. I tested other outlets and equipment from the panel and it seems like this doesnt happen on anything feed from b or c phase but only on a phase. I am kinda scratching my head at the moment and Any insite would be appriciated.
thanks!