if the utility companies allow a 600A commercial 4-gang/ meter service that has no main ocpd
to have (4) 200A tenant OCPDs
or,
the total, sum all ocpds shall not exceed 600A ????????

Thank you
 

sameguy

Senior Member
Location
New York
Occupation
Master Elec./JW retired
I'm going no.
800a with "you" being responsible to insure only 600a on their potential, no.
Better price up a big old disco and call the poco.
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
The utility companies around here want to know the load and what size service conductor you use. That's pretty much it.
Maybe, just maybe, if you show load greater than the rating of the meter socket they might question it.
What you describe is pretty common here.
 

Iron_Ben

Senior Member
Location
Lancaster, PA
Hi ,
wondering,
if the utility companies allow a 600A commercial 4-gang/ meter service that has no main ocpd
to have (4) 200A tenant OCPDs
or,
the total, sum all ocpds shall not exceed 600A ????????

Thank you

Each utility makes its own rules, to an extent. We hooked up installations like you describe routinely.
 
I dont see why not, although I dont recall even seeing 6 gang meter socket with no OCPD's. I have used/done 4 gang with no OCPD's and those are rated 200A per position. You can always use individual sockets too, nothing says that have to be ganged. Of course I cant speak for you POCO rules.
 