Re: Above ground diesel tanks
Most inspectors, insurance, fire, and electrical like to require tanks for diesel to be wired per article 514. I fully understand diesel fuel is a combustible liquid and not a flammable liquid, and therefore its presence does not require any classification per 501 and 514.3(B). The problem arises in the interpretation of Motor Fuel Dispensing Facilities, and their intended use, and their actual use. When that tank is filled with a flammable liquid, I didn't say if, the hazards of the electrical system being the ignition source for an explosion are very real.
At the very least, insurance companies like to reduce their risks, and do not like to allow the tanks to be unclassified.
Fred Bender