Above-ground Pipe rack with no Electrical components

Status
Not open for further replies.

wsbeih

Member
Location
USA
We have a steel pipe rack (~25ft high) recently constructed for piping support only. There are no Electrical raceways or enclosures supported through this rack.
This rack is not grounded to earth.
My question is: is it really needed/mandated by code? knowing that there are no electrical component/equipment supported by this rack?
 
It is not required by the electrical code. It is often required for industrial projects by the project specs.
 