Above Ground Pool Pump

Tav1980

Member
Location
MD
Occupation
Electrical
For an above ground pool pump, does it need to be connected to a equippotential bonding grid, or will a GCFI suffice without bonding? I ask because the pool pump I am working on does not have a equippotential bonding grid. I have read the NEC, but would like some extra advice. Thanks!
 
Also notice 680.26(B)(6). If the pool pump is double insulated, it won't have a bonding lug. This is the best choice for a pool that doesn't require an equipotential bonding grid and many above ground pools come with pumps like this. If the pump has a lug and the grid isn't required, then there is nothing to do with that lug. If it has a grid and you have a double insulated pool pump with no bonding lug, then part (a) of the exception tells you to connect the equipotential grid to the motor circuit EGC if it isn't connected to an EGC elsewhere.
 
Also notice 680.26(B)(6). If the pool pump is double insulated, it won't have a bonding lug. This is the best choice for a pool that doesn't require an equipotential bonding grid and many above ground pools come with pumps like this. If the pump has a lug and the grid isn't required, then there is nothing to do with that lug. If it has a grid and you have a double insulated pool pump with no bonding lug, then part (a) of the exception tells you to connect the equipotential grid to the motor circuit EGC if it isn't connected to an EGC elsewhere.
Thank you! This I came to this conclusion as well. Your reply solidified it. I appreciate it!
 