Hi, it's been a couple or four years since I did a pool.In NJ we are using the 2017 nec and last pools I did was 2014 nec.
In reviewing between the two I have some questions. (residential, one family)
Motors. 680.21(A)(1)
2014 insulated equipment grounding conductor, (A)(4) one family interior ground is permitted to be uninsulated.
2017 insulted equipment ground only in corrosive environment, non corrosive can be uninsulated, (A)(4) is gone.
Does 2017 remove the required insulated equipment ground for the exterior from the house to the pool motor as well?
Lighting, Receptacle, and Equipment 680.22 (A)(2)(1)
2014 single receptacle
2017 no mention of receptacle
Can I assume that pump receptacle can be a duplex receptacle (if wired for 120v).
( where is twistlock, is that pre2014? The ones I did a few years back were built in pools and the breakers in a pool panel where the disconnect)
Underwater Luminaires 680.23 (F) (1) Branch circuit Wiring (There is no lighting for this above ground pool, just reviewing)
2014 interior and exterior insulated equipment ground.
2017 corrosive condition requires insulated equipment ground. non corrosive can be uninsulated.
Does 2017 remove the required insulated equipment ground for interior and exterior from the house to the pool lighting as well?
Feeders 680.25 (A) (There is no feeder for this above ground pool, just reviewing)
Is this correct?
Question about the filter pump motor controller (Time clock)
Does this Timer need to be located by the motor or can it be located indoors at the panel?
Thank you
Is this correct?
Thank you