Cavie
Senior Member
- Location
- SW Florida
We are having a differance of opinion in the office as to when a pool is storeable or perminent. ART #680 states that a pool is permenent when partially in the ground or when it is capible of holding water more than 42" deep. The lead man says that if an above ground pool is "Listed" to be partially in the ground, it still remains an above ground storable pool not subject to Equipotential bonding or bonding of the pool walls or motor.
I and others say that it is a perminent pool and does require a bonding grid And the walls need bonding. This pool in question also has a aluminium cage built on top of the wooden deck that needs bonding. the pump is 100' away from the pool.
680.26 (B) (4) states that the EB must also be run to the double insulated pump for future pump replacement. The EB must be connected to the Grounding circuit of the pump reciptical.
Am I reading this correctly???