Above ground swimming pool.. Voltage drop and convenience outlet

Status
Not open for further replies.

Marknewjersey

Member
Location
USA New Jersey
Occupation
Electrician
Hi guys

150 of run.. From panel to to the outlet for the pump for the swimming pool above ground .. Do we need to go by the voltage drop code.. I.e. Should we use #10 since it's a long run or #12 will do the job to pass inspection.

2. Can we use the same circuit of the pump for the convenience outlet by the pool

Thank you
 

tom baker

First Chief Moderator & NEC Expert
Staff member
Location
Bremerton, Washington
Occupation
Master Electrician
1. There is no code requirement for voltage drop, only an info note. But voltage drop creates heat and the customer pays for that.
2. Maybe. How many amps is pump and what voltage?
Why not run an extra 2 wires for receptacle?
 

Dsg319

Senior Member
Location
West Virginia
Occupation
Wv Master “lectrician”
Hi guys

150 of run.. From panel to to the outlet for the pump for the swimming pool above ground .. Do we need to go by the voltage drop code.. I.e. Should we use #10 since it's a long run or #12 will do the job to pass inspection.

2. Can we use the same circuit of the pump for the convenience outlet by the pool

Thank you
Idk the answer to your second question. But voltage drop is only a recommendation of the NEC.
So therefor I would recommend doing a voltage drop calculation. Another thing to keep in mind is when your not within voltage drop recommendations, it will probably take longer to clear ground faults leaving conductive surfaces energized longer. So I would do a calculation or get a good app to throw your numbers in and check.
 

Marknewjersey

Member
Location
USA New Jersey
Occupation
Electrician
1. There is no code requirement for voltage drop, only an info note. But voltage drop creates heat and the customer pays for that.
2. Maybe. How many amps is pump and what voltage?
Why not run an extra 2 wires for receptacle?
The number 12 wire for 12 gauge is good if I run two wires
 
Location
NE (9.06 miles @5.9 Degrees from Winged Horses)
Occupation
EC - retired
VD upon a ground fault should not be a concern IF you are using GFCI protection on those circuits. I believe they are a requirement for your pool equipment and outlet.


Idk the answer to your second question. But voltage drop is only a recommendation of the NEC.
So therefor I would recommend doing a voltage drop calculation. Another thing to keep in mind is when your not within voltage drop recommendations, it will probably take longer to clear ground faults leaving conductive surfaces energized longer. So I would do a calculation or get a good app to throw your numbers in and check.
 

Dsg319

Senior Member
Location
West Virginia
Occupation
Wv Master “lectrician”
VD upon a ground fault should not be a concern IF you are using GFCI protection on those circuits. I believe they are a requirement for your pool equipment and outlet.
Very True I never thought about GFCI protection to be there anyways.
 