Absorbing VARs vs Generating VARs industry definition

Merry Christmas
Status
Not open for further replies.

mbrooke

Batteries Included
Location
United States
Occupation
Technician
Brain freeze... These two seem to contradict each other and I'd say the latter is correct, but can the prior also be correct since it does not explicitly speak about synchronous rotating generators? Which is industry correct for that matter? I'm confused to be honest. :confused:


1)

1629870251922.png




2)

1629870184635.png
 

David Castor

Senior Member
Location
Washington, USA
Occupation
Electrical Engineer
If the real power (kW) and the reactive power (VARs) are flowing in the same direction, it is LAGGING. If the two are flowing in opposite directions it is LEADING. That's all you need to know.

So a generator that is producing real kw and vars is lagging. If it is absorbing vars while producing kW it is leading.

A typical induction motor is consuming kW and Vars, so it is lagging. A synchronous motor consuming kW but producing VArs is leading.
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
romex jockey is correct but anyone wanting to participate in the conversation is welcome to do so.