J j rae Senior Member Mar 13, 2012 #1 Can you run AC ckt conductors in the samd conduit as Dc fire alarm plenum cables rated at 300volts? What code number?
Can you run AC ckt conductors in the samd conduit as Dc fire alarm plenum cables rated at 300volts? What code number?
dhalleron Senior Member Location Louisville, KY Occupation Master Electrician/Senior Fire Alarm Technician Mar 13, 2012 #2 NFPA 70 2008 760.136. Normally no, unless 760.136 (D) Associated Systems Within Enclosures helps you. Is this a power limited fire alarm circuit or non power limited? Also the manufacturer may have instructions requiring separation. Last edited: Mar 13, 2012
NFPA 70 2008 760.136. Normally no, unless 760.136 (D) Associated Systems Within Enclosures helps you. Is this a power limited fire alarm circuit or non power limited? Also the manufacturer may have instructions requiring separation.