In PV systems, you must calculate the output current of the inverter *1.25, to select the correct wire. But when you are going to calculate voltage drops, Do we need to multiply the power of the inverter * 1.25 to do this calculation?
Hi
In PV systems, you must calculate the output current of the inverter *1.25, to select the correct wire. But when you are going to calculate voltage drops, Do we need to multiply the power of the inverter * 1.25 to do this calculation?
...On a power optimizer's system, it is based off nominal operating string voltage and the current that corresponds to the array's STC power at that voltage.
1.25 is not always required too see the code section you can just correct and adjust it for temperature and use instead. Also you can use a 100 percent rated breaker.Hi
In PV systems, you must calculate the output current of the inverter *1.25, to select the correct wire. But when you are going to calculate voltage drops, Do we need to multiply the power of the inverter * 1.25 to do this calculation?
1.25 is not always required too see the code section you can just correct and adjust it for temperature and use instead. Also you can use a 100 percent rated breaker.
Sent from my SM-N920V using Tapatalk