If I were to use one which one would be the best all around to keep on the truck?
HUH?Originally posted by mc5w:
Type AC is also a pain in the rear end because the #16 aluminum ground strip has to be connected to the equipment grounding conductors and not just laid back along the cable and then depend upon cable clamps to make contact.
The armor of Type AC cable is recognized as an equipment grounding conductor by 250.118. The required internal bonding strip can be simply cut off at the termination of the armored cable, or it can be bent back on the armor. It is not necessary to connect it to an equipment grounding terminal. It reduces the inductive reactance of the spiral armor and increases the armor's effectiveness as an equipment ground. Many installers use this strip to help prevent the insulating bushing required by 320.40 (the ?red head?) from falling out during rough wiring.