AC cable

Status
Not open for further replies.

iwire

Moderator
Staff member
Location
Massachusetts
Re: AC cable

There is no 'proper' termination of the bonding strip.

Cut it off flush, back wrap it, what ever you want to do. :cool:
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Re: AC cable

Bob is correct. The metal bonding strip is required to be in contact with the outer metallic jacket of the cable and is not required to be terminated in any specific way. Within type AC cable, the bonding strip allows the use of the outer jacket as a listed grounding conductor.
 

iwire

Moderator
Staff member
Location
Massachusetts
Re: AC cable

Originally posted by sparkslord:
Inspectors have told me they want at least 6" of wire wrapped back around the shield.
They can ask for anything, you only have to give them what is required by code.

You will not find an NEC section that requires you to back wrap it.

Of course you can if you want to, it is a nice redhead holder. :)
 

pierre

Senior Member
Re: AC cable

NEMA has a 'paper' (the name of it slips my mind) of how to terminate the bonding conductor for MC and AC cable.
There is no NEC requirement - the inspector who is asking this, shows his ignorance and misconception of the purpose for the bonding conductor in the AC cable.
 