AC circuit breaker size

Status
Not open for further replies.

russ57

Member
On the data plate of an AC compressor it states MAXIMUM of 25 amps of protection. A 30 amp breaker is installed. Is this correct? If so what code is it. Thanks in advance...

Russ
 
Re: AC circuit breaker size

430.52 would apply to the rating of the motor alone. When the manufacturer specs an overcurrent rating, it's already taken into account however.
 
Re: AC circuit breaker size

If you read the nameplate of an AC unit, all of the information is given to you to size the circuit and the short circuit and ground fault protective device (breaker or fuse). This is done because so many heating and AC contractors don't have a clue about how to size the components but they can run a circuit and install an overcurrent device. This makes it foolproof for them . . . sorta. :D
 
Re: AC circuit breaker size

Charlie is correct. Article 440 does not allow for rounding up of the OCPD. Additionally, 440 applies to hermetic refrigerant motor-compressors, not to any old motor driving a compressor. Hermetic sealed motor-compressors don't have an external motor with a drive belt. The motor-compressor is cooled by the refrigerant.

Second thought, unless the nameplate specifically says breaker or fuse, you are often limited to fuse protection only.
 
Re: AC circuit breaker size

Actually, if the nameplate doesn't say anything, you are permitted to use either a circuit breaker or fuse. Some nameplates say maximum fuse size and you are required to use only a fuse. Some say fuse or HACR circuit breaker, that restricts the circuit breaker to a HACR type or a fuse. :D
 