Charlie is correct. Article 440 does not allow for rounding up of the OCPD. Additionally, 440 applies to hermetic refrigerant motor-compressors, not to any old motor driving a compressor. Hermetic sealed motor-compressors don't have an external motor with a drive belt. The motor-compressor is cooled by the refrigerant.
Second thought, unless the nameplate specifically says breaker or fuse, you are often limited to fuse protection only.