I've heard talk on this forum that you may see a #12 wire on a 50 amp breaker feeding an Air Conditioner.
Most Residential Air Conditioners that I have hooked up just have a 2 or 3p contactor on them and the Overload if any is a Thermal overload that is laying against the face of the Compressor Motor. Not A full blown Starter with Heaters. I would think that this Thermal Overload is just a last line of Defense to take the compressor off line before destruction of the Compressor.I dont consider this like a set of overloads on a starter where there is a set amperage at which the contactor will drop out and protect the wire. I dont agree that a Thermal Overload that doesnt have a set trip point to Open,is an acceptable means of protecting the wire that feeds the unit.
Therefore I would think you would have to be very careful where you applied
the wire being protected for the simple fact that it has a Thermal Overload on it.
Most Residential Air Conditioners that I have hooked up just have a 2 or 3p contactor on them and the Overload if any is a Thermal overload that is laying against the face of the Compressor Motor. Not A full blown Starter with Heaters. I would think that this Thermal Overload is just a last line of Defense to take the compressor off line before destruction of the Compressor.I dont consider this like a set of overloads on a starter where there is a set amperage at which the contactor will drop out and protect the wire. I dont agree that a Thermal Overload that doesnt have a set trip point to Open,is an acceptable means of protecting the wire that feeds the unit.