Re: AC Condensing units
Originally posted by stew:
Where in the code does it say that the 25% is already figured in or is this just what an experienced guru such as an i wire just knows?
First off that is code geek, not guru.
I think that we should start at where the 'extra' 25% is required for HVAC units.
One place would be 440.32
440.32 Single Motor-Compressor.
Branch-circuit conductors supplying a single motor-compressor shall have an ampacity not less than 125 percent of either the motor-compressor rated-load current or the branch-circuit selection current, whichever is greater.
For a wye-start, delta-run connected motor-compressor, the selection of branch-circuit conductors between the controller and the motor-compressor shall be permitted to be based on 58 percent of either the motor-compressor rated-load current or the branch-circuit selection current, whichever is greater.
Notice that section only applies to Single Motor-Compressor.
The same basic requirement is also in 440.33 Motor-Compressor(s) With or Without Additional Motor Loads.
Neither of those sections apply to the HVAC units that we normally install, the section that does apply is 440.35.
440.35 Multimotor and Combination-Load Equipment.
The ampacity of the conductors supplying multimotor and combination-load equipment shall not be less than the minimum circuit ampacity marked on the equipment in accordance with 440.4(B).
In this section you will notice the absence of the 25% extra required for single compressors or Motor-Compressor(s) With or Without Additional Motor Loads.
You will also notice it references 440.4(B) which basically says the manufacturer will be responsible for the calculations and mark the unit with the minimum supply circuit conductor ampacity, and the maximum rating of the branch-circuit short-circuit and ground-fault protective device.
A unit marked with an minimum supply circuit conductor ampacity of 20 amps and a maximum branch-circuit short-circuit and ground-fault protective device of 35 could be wired with 14/2 NM and a 35 amp breaker.
We use nm all the time for this and if in a home run it as normal and when it emerges we run it out a pvc lb and pc to the disc.
I have some bad news for you here, if you are running the NM in the PVC outside you have a violation.
NM is not rated for wet locations, outdoor raceways are wet locations.