I have discussion with my coworker.
The story is: we need to do a apartment load calculation.
Each apartment has indoor fan coil (power come from each apartment's panel), and group of apartment share one outdoor condensing unit (power from building's panel). HVAC contractor/supplier will collect and provide data for tenant billing.
The problem is: we want to use optional method to calculate the meter bank. The argument is: is indoor fan coil an air conditioning?
in order to use optional method, we need to meet following code.
The code I citied is 2008 NEC code.
220.84 (A)(3)
Each dwelling unit is equipped with either electric
space heating or air conditioning, or both. Feeders and
service conductors whose calculated load is determined
by this optional calculation shall be permitted to have
the neutral load determined by 220.61.
Let me know your opinion. And why?
The story is: we need to do a apartment load calculation.
Each apartment has indoor fan coil (power come from each apartment's panel), and group of apartment share one outdoor condensing unit (power from building's panel). HVAC contractor/supplier will collect and provide data for tenant billing.
The problem is: we want to use optional method to calculate the meter bank. The argument is: is indoor fan coil an air conditioning?
in order to use optional method, we need to meet following code.
The code I citied is 2008 NEC code.
220.84 (A)(3)
Each dwelling unit is equipped with either electric
space heating or air conditioning, or both. Feeders and
service conductors whose calculated load is determined
by this optional calculation shall be permitted to have
the neutral load determined by 220.61.
Let me know your opinion. And why?