Hey folks, I have a question.
I have an Air Handler with a nameplate that has:
Min Ckt Ampacity: 17.6 A
Maximum Fuse or HACR Type Circuit Breaker: 30 A
Is it ok to put a #12 AWG MC Cable with a 25A breaker to this?
How about:
Min Ckt Ampacity: 29.8 A
Maximum Fuse or HACR Type Circuit Breaker: 50 A
with a #10 AWG and a 45 A breaker?
It seems like this configuration should be ok, since it follows the nameplate, but which part of the code allows this? It seems like it violates the "#12 with a 20 A breaker" rule from 310.16.
Also, FYI, this is residential.
Thanks in advance for the help!
I have an Air Handler with a nameplate that has:
Min Ckt Ampacity: 17.6 A
Maximum Fuse or HACR Type Circuit Breaker: 30 A
Is it ok to put a #12 AWG MC Cable with a 25A breaker to this?
How about:
Min Ckt Ampacity: 29.8 A
Maximum Fuse or HACR Type Circuit Breaker: 50 A
with a #10 AWG and a 45 A breaker?
It seems like this configuration should be ok, since it follows the nameplate, but which part of the code allows this? It seems like it violates the "#12 with a 20 A breaker" rule from 310.16.
Also, FYI, this is residential.
Thanks in advance for the help!