AC & DC in same conduit

Status
Not open for further replies.

j rae

Senior Member
Can we run AC &DC fire alarm ckts in the same conduit?? Some conduits are less than 1 foot long between the panel and the transmiter. The DC signal cable is type size 14 NEC TYPE FPLP . Can you give me the code referance?? THANKS
 
Do you mean AC (120V to power the FA panel) and DC(FA circuits)? I don't think so.

If you meant AC(24V control circuits) and DC (FA initiation circuits) I'm pretty sure you're OK.

Can we run AC &DC fire alarm ckts in the same conduit?? Some conduits are less than 1 foot long between the panel and the transmiter. The DC signal cable is type size 14 NEC TYPE FPLP . Can you give me the code referance?? THANKS
 
Do you mean AC (120V to power the FA panel) and DC(FA circuits)? I don't think so.

If you meant AC(24V control circuits) and DC (FA initiation circuits) I'm pretty sure you're OK.

No 120 volt ckt and 24v dc
 