AC/DC wires in same conduit for Generac generator

Twebber1812

New User
Location
Morris, IL
Occupation
Journeyman Electrician
I have been installing generators for close to 8 years. I figure somewhere in the neighborhood of 1,500 generators. The company has existed for 20 years prior to me. I have always run a single conduit from the ATS to the generator, and pulled the feeder and control wires all in the same conduit. This is how Generac always did it when purchasing an ATS with a prewired whip. This is the same way that the tray cable sold by cablemaster does it as well. I had an inspector the other day tell me that wires 194 and 23 that carry dc voltage are not allowed to be in the conduit with the control wires that carry ac voltage. I'm fairly confident he is wrong; i'm just not sure how to prove it. any thoughts?
 

Mr. Serious

Senior Member
Location
Oklahoma, USA
Occupation
Electrical Contractor
Are these control wires considered a Class 2 or Class 3 circuit? If so, I believe 725.136 (D) applies. It allows them to be routed within the same conduit under certain conditions. They must be associated with the same equipment as the power conductors and they must have certain insulation types or be installed using Class 1 wiring methods.

Or if they're considered a Class 1 circuit, 725.48 still permits them within the same conduit if they're functionally associated.
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
Many years go, Generac specified separate conduits for the feeder and for the control wires, even though they were combined in their whip, but the AC and DC control wires were still run together.

I run them all in one conduit unless there is a good reason not to.
 

David Castor

Senior Member
Location
Washington, USA
Occupation
Electrical Engineer
As long as the dc wiring is insulated at the level of the maximum ac voltage, the NEC allows it (up to 600 V). It could be a requirement or recommendation of the supplier if there are concerns about electrical interference. Just because the NEC allows it doesn't mean it will always work.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
As long as the dc wiring is insulated at the level of the maximum ac voltage, the NEC allows it (up to 600 V). It could be a requirement or recommendation of the supplier if there are concerns about electrical interference. Just because the NEC allows it doesn't mean it will always work.
It really depends on how the control circuit is classified and not not the insulation rating of the conductors.
 

tortuga

Code Historian
Location
Oregon
Occupation
Electrical Design
This is the same way that the tray cable sold by cablemaster does it as well.
As others have said if your using 600V tray cable or TFFN/THWN that is compliant,
If not read on.
It really depends on how the control circuit is classified and not not the insulation rating of the conductors.
In the manufacturers instructions for the Generacs I installed it says:
"NOTE: This wiring can be run in the same conduit if the appropriate insulation rated wire is used."
Unfortunately some installers take that to mean 18AWG 'door bell' cable along with the 600V rated conductors can be used.
IMO it would be a violation to use anything other than 600V rated conductors, and not an uncommon violation at that.
I have even seen a few 'professional' installs where the installer pulled cat5 for the control circuit.
look at the installation instructions under electrical:
g.png
 

solarken

NABCEP PVIP
Location
Hudson, OH, USA
Occupation
Solar Design and Installation Professional
According to Generac transfer switch manual, the dry contact 2-wire start is a class 1 signaling circuit, which would fall under 725.41(B). The conductor requirements in 725.49 permits 18AWG or 16AWG and larger, with insulation voltages rated for the system voltage and not less than 600V. 725.48(B)(1) permits class 1 circuits to be installed in the same conduit or cable with power-supply circuits. I believe the inspector is incorrect.
 

hillbilly1

Senior Member
Location
North Georgia mountains
Occupation
Owner/electrical contractor
As others have said if your using 600V tray cable or TFFN/THWN that is compliant,
If not read on.

In the manufacturers instructions for the Generacs I installed it says:
"NOTE: This wiring can be run in the same conduit if the appropriate insulation rated wire is used."
Unfortunately some installers take that to mean 18AWG 'door bell' cable along with the 600V rated conductors can be used.
IMO it would be a violation to use anything other than 600V rated conductors, and not an uncommon violation at that.
I have even seen a few 'professional' installs where the installer pulled cat5 for the control circuit.
look at the installation instructions under electrical:
View attachment 2569926
I’ve come behind some where they used thermostat wire for ALL of the control wires! I don’t think they realized four of the six are line voltage. (On the older models) Sense wires were 240, charger was 240, and they only had two dc wires which powered the transfer relay. Then newer ones are as the above chart.
 

tortuga

Code Historian
Location
Oregon
Occupation
Electrical Design
I’ve come behind some where they used thermostat wire for ALL of the control wires! I don’t think they realized four of the six are line voltage. (On the older models) Sense wires were 240, charger was 240, and they only had two dc wires which powered the transfer relay. Then newer ones are as the above chart.
Well at least they did not use cat5 like the 'professionals' around here used.
According to Generac transfer switch manual, the dry contact 2-wire start is a class 1 signaling circuit
Thats interesting do you have a source for that?
If they classified it as class 1 from the getgo then a chapter 3 wiring method would be required.
 

solarken

NABCEP PVIP
Location
Hudson, OH, USA
Occupation
Solar Design and Installation Professional
Well at least they did not use cat5 like the 'professionals' around here used.

Thats interesting do you have a source for that?
If they classified it as class 1 from the getgo then a chapter 3 wiring method would be required.
I just looked at a typical Generac transfer switch manual, like this one. It's on page 7.
 

David Castor

Senior Member
Location
Washington, USA
Occupation
Electrical Engineer
It really depends on how the control circuit is classified and not not the insulation rating of the conductors.

I've never seen one that wasn't Class 1, which can be in the same raceway as the power circuit as long as insulated at the appropriate level. But I'm not involved in residential work (other than my own residence), so maybe these are different.
 

farmantenna

Senior Member
Location
mass
It really depends on how the control circuit is classified and not not the insulation rating of the conductors.
bingo! this is the correct anwser. What class? not voltage insulation. Generac specifically states in their instructions that the control wires are a class1circuit and can all be in the same cable assembly(which they sell) or conduit.
 
On this topic, and out of curiosity: I watched a YouTube video on a Generator installation in Canada. They said that if the control wires were in the same conduit as the power they needed to be shielded. Is that a CEC thing, hogwash, or a manufacturer thing?
 

solarken

NABCEP PVIP
Location
Hudson, OH, USA
Occupation
Solar Design and Installation Professional
bingo! this is the correct anwser. What class? not voltage insulation. Generac specifically states in their instructions that the control wires are a class1circuit and can all be in the same cable assembly(which they sell) or conduit.
The voltage rating of the insulation is still relevant, and needs to be at least rated for the system voltage contained in the same cable or raceway, and not less than 600V. See 725.49(B).
 

solarken

NABCEP PVIP
Location
Hudson, OH, USA
Occupation
Solar Design and Installation Professional
On this topic, and out of curiosity: I watched a YouTube video on a Generator installation in Canada. They said that if the control wires were in the same conduit as the power they needed to be shielded. Is that a CEC thing, hogwash, or a manufacturer thing?
I am not aware of a code requirement for shielding, but when putting control wiring in with power conductors, the type of control signal is important when considering shielding. For a two-wire start/dry contact control like discussed here, there is not reason for shielding, as it would not be likely that any noise from the power conductors could affect the open or closed contact signal. For analog control signals, like low voltage current transformer signals, especially for low voltage signals that travel from/to high impedance sources and inputs, it is more likely. At least that is my view.
 