What are the clearances for a disconnect for a condensing unit outdoor
Sent from my SM-G920T using Tapatalk
Sent from my SM-G920T using Tapatalk
I thought since a breaker controlled the disconnect 110.26 didn't apply
Sent from my SM-G920T using Tapatalk
I thought since a breaker controlled the disconnect 110.26 didn't apply
Sent from my SM-G920T using Tapatalk
AHJ is saying 30 inches I was hoping I could find some help as I don't have 30 inches on most of these units
Sent from my SM-G920T using Tapatalk
AHJ is saying 30 inches I was hoping I could find some help as I don't have 30 inches on most of these units
Sent from my SM-G920T using Tapatalk
To do a hot-dead-hot check on the feed to the A/C?Why would you work on an energized disconnect when there is a breaker controlling it. The disconnect is just a means to make the condensing unit you plan to work on not energized.
Sent from my SM-G920T using Tapatalk
To do a hot-dead-hot check on the feed to the A/C?
The load side of the local disconnect, fused or not, would be the very first place where many service techs would check for power if there was a service call. Based on that, many AHJs required 110.26 work spaces for a disconnect at a AC unit.
The load side of the local disconnect, fused or not, would be the very first place where many service techs would check for power if there was a service call. Based on that, many AHJs required 110.26 work spaces for a disconnect at a AC unit.