I have an 208 3 phase 125 amp breaker feeding a 60 amp ac disconnect on roof top ac unit. I have to remove for a roofer to do some work around unit. Once I put back want to use a 3 phase fused disconnect but I’m unsure about sizing Of disconnect.
I have read through 440.12 but it doesn’t makes sense to have such large breaker before such a small disconnect. shouldn’t it be rated according to breaker then fused down to accommodate the unit which is 50 amps. And yes I’ve considered a new breaker, but just curious about this. This is an existing mess which I’m trying to clean up.
I have read through 440.12 but it doesn’t makes sense to have such large breaker before such a small disconnect. shouldn’t it be rated according to breaker then fused down to accommodate the unit which is 50 amps. And yes I’ve considered a new breaker, but just curious about this. This is an existing mess which I’m trying to clean up.