Main panel is 400 amps. There is a #4 cu feeder for one AC unit. The feeder goes to an EXO box, 60 amp rating with 45 amp fuses as required by manufacturer protecting #6 Cu wire to the AC unit . The full load amp rating is 41 amps. Can I install a 100 amp circuit breaker in the 400 amp box for the #4 wire feeder based on NEC 440-22, the 225% rule for AC? 41 x 225% = 92 amps, next size up is 100 amps. If not what circuit breaker should I use? Everything is 3 phase.