AC Feeders

Mike is a sponsor of the forum but I don't think he participates.

And you would use article 220.

Easiest way is to calculate the kw with MCA and rated voltage. Add them up. Do your calculation to get the current and there you go. We would need the # of condensers and the nameplate data voltage, phase and MCA.
 
And you would use article 220.

Easiest way is to calculate the kw with MCA and rated voltage. Add them up. Do your calculation to get the current and there you go. We would need the # of condensers and the nameplate data voltage, phase and MCA.
Why would you use the MCA for each unit? The MCA already has a 25% factor added to it for the largest load of each unit. Wouldn't you need to only use the 25% adder just once?
 