Although an ac high potential test is recommended, a dc test may be performed if only a dc test unit is available.
In this case the equipment must be capable of delivering 5 milliamperes for one minute. When a DC test voltage is used, a high field emission current from a microscopic sharp spot on one contact can be misinterpreted as a sign of a vacuum interrupter filled with air.
To avoid a misinterpreted test result, the open interrupter should always be subjected to both voltage polarities. That is, apply the DC Voltage:
- first, so that one contact of the interrupter is the cathode, and
- second, so that the other contact of the interrupter is the cathode.
A bad interrupter filled with air will have a similarly high leakage current in both polarities. A good interrupter with a good vacuum level may still have a high leakage current, but this will generally be in only one polarity. Such an interrupter usually has a tiny sharp spot on one contact that produces a high field emission current when the sharp spot is a cathode, but not on an anode. In addition, such an interrupter would also normally withstand the required AC voltage which is the definitive test of its vacuum integrity