Re: AC Load w/heat strips
Most of the responses you have received in the Forum have some truth in them. There are several things we need to know for a heat pump problem.
First of all, are there supplemental electric heaters integral with the unit and on the same circuit as the indoor unit,
or are the supplemental heaters separate from the heat pump but installed in the duct work and on a different circuit?
Also, as some of the posts in the forum indicate, the efficiency of heat pumps decreases somewhere below 40 degrees F and the supplemental heat may be switched on ? often this happens in increments so all of the electric heat is not employed simultaneously. The heat bank may also be turned on during ?de-icing? to keep the outdoor unit from freezing over in the winter. There are different designs in regard to the way the heat bank functions, so we need to know if the design will allow the heat bank to run simultaneously with the heat pump compressor.
If the electric heat banks are contained within the heat pump unit, with no external heat banks, the manufacturer?s information should help you determine what the maximum heating load is and what the maximum cooling load is, then use the larger of the two.
If the heat banks are separately installed and on separate circuits, you will need to determine if the control circuit allows the heat pump to run simultaneously with the electric heat, and if so you should add the heat pump load to the supplemental heat loads when calculating the heating load.
In colder parts of the country, the additional electric heat banks are essential. In some milder climates, that may not be the case. Also, some of the more efficient systems that use ground water return loops or other geothermal options may not need the supplemental electrical heat in some climates.
When you look for the load on the unit, be sure you use the nameplate load information, not the suggested circuit breaker size, for sizing the electrical service. The manufacturer should have information in the installation manual and possibly on their website to help you determine the specific load requirements for each model.
You are correct in your statement that since all units can be turned on simultaneously, they will all need to be added into the service size. I am not sure what is included in the amperages you have listed, so cannot tell you if that is the correct calculation or not. Make sure you know what the actual load is on each unit, and if electric heat is included. If the electric heat is not included in the heat pump cabinet, are there other circuits supplying separate electric heaters in the ductwork? If so, include them in the heat side of your calculation.
Any feedback on this is welcome, I hope it will be of some help.