I have found that most of the time the only solution to this problem is changes on the utility side of the meter. Transformers are often too far away for reasonable voltage drop at the service, especially if overhead service. POCO's size overhead conductors for what they can carry but usually do not consider voltage drop, especially voltage drop for motor starting.