Just to be sure. Do I need in AC side (solaredge system) the overcurrent device rating---> Inverters amp*1.25? This rule is clear in conductors.
I was reeding again NEC code...
Yes. The 125% factor applies for all inverter output OCPDs, unless the OCPD and all within its enclosure are otherwise listed as continuous duty (which is uncommon).
I understand that there is a 3rd option of a adjustable CB that is my situation. If we have an adjustable CB, that meets 240.6, we just need the nominal amp rating (without *1.25), don´t we?