R relbas Member Jul 5, 2012 #1 I have a name plate with minimum circuit ampacity 18 Amp Maximum fuse size 20 Amp. My question is: Do I bring # 12 wire or #10 wire? Thank you .
I have a name plate with minimum circuit ampacity 18 Amp Maximum fuse size 20 Amp. My question is: Do I bring # 12 wire or #10 wire? Thank you .
beanland Senior Member Location Vancouver, WA Jul 5, 2012 #2 80% in MCA 80% in MCA The 80% derating factor should already be included in the 18A so #12 meets that requirement. The actual load current is probably 14 Amps.
80% in MCA 80% in MCA The 80% derating factor should already be included in the 18A so #12 meets that requirement. The actual load current is probably 14 Amps.
ceb58 Senior Member Location Raeford, NC Jul 5, 2012 #3 relbas said: I have a name plate with minimum circuit ampacity 18 Amp Maximum fuse size 20 Amp. My question is: Do I bring # 12 wire or #10 wire? Thank you . Click to expand... You have a name plate on what?????????????? I see nothing over 20 amp so I will say 12. Never mind I see the AC part. Last edited: Jul 5, 2012
relbas said: I have a name plate with minimum circuit ampacity 18 Amp Maximum fuse size 20 Amp. My question is: Do I bring # 12 wire or #10 wire? Thank you . Click to expand... You have a name plate on what?????????????? I see nothing over 20 amp so I will say 12. Never mind I see the AC part.
infinity Moderator Staff member Location New Jersey Occupation Journeyman Electrician Jul 5, 2012 #4 You could use #14 with the 20 amp OCPD too if you're not using a 60? C wiring method.