Application: We have a direct drive three phase 480V fan listed for 1170 RPM @ 60Hz on a variable frequency drive. We want to over speed the fan to operate at 1770 RPM @ 90 Hz.
Problem: We need to calculate the AC resistance of the conductors serving fan when operating at 90Hz.
The formula for AC resistance is as follows:
RAC= RDC * ( 1 + Ys + Yp )
YS = Skin Effect Factor
YP = Proximity Effect Factor (Three Conductors)
Ys = (2 * μ * f * ks / RDC )2 / (192 + (2 * μ * f * ks / RDC )2 )
z = (2 * μ * f * ks / RDC )2 / (192 + 0.8 * (2 * μ * f * ks / RDC )2 ) - Intermediate calculation
Yp = z * (d / s)2 * [ 0.312 * (d / s)2 + 1.18 / (z + 0.27) ]
μ (Magnetic Permiability of Free Air) = 1.2566 x 10-7
ks (Construction Factor) = 1
f = frequency (Hertz)
d = diameter of conductor
s = spacing between conductor centers
Referring to NEC Chapter 9, Table 9 - AC Resistance of copper conductors in PVC Conduit at 75 Deg C / 60 Hz, the following values are listed:
#6 - 0.4900 Ohms / 1000 Ft
#4 - 0.3100 Ohms / 1000 Ft
#3 - 0.2500 Ohms / 1000 Ft
#2 - 0.1900 Ohms / 1000 Ft
#1 - 0.1500 Ohms / 1000 Ft
Referring to NEC Chapter 9, Table 8 - DC Resistance of uncoated copper conductors at 75 Deg C, the following values are listed:
#6 - 0.4910 Ohms / 1000 Ft
#4 - 0.3080 Ohms / 1000 Ft
#3 - 0.2450 Ohms / 1000 Ft
#2 - 0.1940 Ohms / 1000 Ft
#1 - 0.1540 Ohms / 1000 Ft
The first problem that I have is that the AC resistance numbers listed in the NEC are in many cases smaller than the DC resistances listed. For instance, the NEC lists the AC resistance of #6 at 0.490 Ohms / 1000 Ft and the DC resistance at the larger value of 0.4910 Ohms / 1000 Ft. I don't see how that is possible given that the formulas I am using for the skin effect factor and proximity effect factor should generate positive values.
What is the formula that the NEC uses to calculate AC resistance, and how do I modify it to adjust for an operating frequency other than 60 Hz?
Problem: We need to calculate the AC resistance of the conductors serving fan when operating at 90Hz.
The formula for AC resistance is as follows:
RAC= RDC * ( 1 + Ys + Yp )
YS = Skin Effect Factor
YP = Proximity Effect Factor (Three Conductors)
Ys = (2 * μ * f * ks / RDC )2 / (192 + (2 * μ * f * ks / RDC )2 )
z = (2 * μ * f * ks / RDC )2 / (192 + 0.8 * (2 * μ * f * ks / RDC )2 ) - Intermediate calculation
Yp = z * (d / s)2 * [ 0.312 * (d / s)2 + 1.18 / (z + 0.27) ]
μ (Magnetic Permiability of Free Air) = 1.2566 x 10-7
ks (Construction Factor) = 1
f = frequency (Hertz)
d = diameter of conductor
s = spacing between conductor centers
Referring to NEC Chapter 9, Table 9 - AC Resistance of copper conductors in PVC Conduit at 75 Deg C / 60 Hz, the following values are listed:
#6 - 0.4900 Ohms / 1000 Ft
#4 - 0.3100 Ohms / 1000 Ft
#3 - 0.2500 Ohms / 1000 Ft
#2 - 0.1900 Ohms / 1000 Ft
#1 - 0.1500 Ohms / 1000 Ft
Referring to NEC Chapter 9, Table 8 - DC Resistance of uncoated copper conductors at 75 Deg C, the following values are listed:
#6 - 0.4910 Ohms / 1000 Ft
#4 - 0.3080 Ohms / 1000 Ft
#3 - 0.2450 Ohms / 1000 Ft
#2 - 0.1940 Ohms / 1000 Ft
#1 - 0.1540 Ohms / 1000 Ft
The first problem that I have is that the AC resistance numbers listed in the NEC are in many cases smaller than the DC resistances listed. For instance, the NEC lists the AC resistance of #6 at 0.490 Ohms / 1000 Ft and the DC resistance at the larger value of 0.4910 Ohms / 1000 Ft. I don't see how that is possible given that the formulas I am using for the skin effect factor and proximity effect factor should generate positive values.
What is the formula that the NEC uses to calculate AC resistance, and how do I modify it to adjust for an operating frequency other than 60 Hz?