hhsting
- Glen bunie, md, us
- Junior plan reviewer
Following disconnect is used as tap ahead of service disconnect for solar install. Is the disconnect in below link suitable to use as service disconnect or not?
See https://www.se.com/us/en/faqs/FA272365/
My conclusion is that QO24L70S is SUSE, as it is not on the list of exceptions in above. Would be a bit tricky to pull off:
I don't see a service entrance barrier in Square D's catalog for the main lugs on that panel, so you'd have to backfeed the breaker and use the barrier for backfed breakers, PKSB1QOBF. Then the backfed breaker would need a hold down kit, which I believe would be PK2MB, although QO24L70S is not listed in the catalog as one of the panels for which that product fits, so it would be necessary to verify that it is compatible.
Cheers, Wayne
Sure, but it's a panelboard being used as a service disconnect, not a problem.this is disconnect not panelboard.
I don't believe there's any prohibition on using a backfed breaker for a service disconnect. But there is a requirement to guard the line side connections on the service disconnect. Unless Square D makes a guard for the line side lugs on QO24L70S, which I didn't see it in their catalog, the only guarding option from them is to use their guard for the terminals on a backfed breaker, PKSB1QOBF.Also your post it says yea Q024L70S SUSE but then says need to backfeed breaker
Anyway, if you want a more knowledgeable answer, you'll probably have to call Square D technical support, they have been pretty helpful in the past.
Cheers, Wayne
Yes, I understand. That makes it a second service disconnect.In my case it is connected on the line side of main service disconnect means.
Indeed, and if you read the reference in my first post, it states that with a few exceptions "All QO single and three phase and HOM load centers are marked as "Suitable for use as Service Equipment" if equipped with integral main breaker or when not more than six disconnecting means are provided." The QO24L70S was not on the list of exceptions, and with only 2 spaces, it obviously has less than six disconnecting means. [The 2020 NEC add a limit of one disconnecting means per enclosure, which the proposed install complies with.]I thought requirement in my case is disconnect needs to be suitable for service disconnecting means?
They need to update the information, as starting with the 2020 you can no longer do that.Yes, I understand. That makes it a second service disconnect.
If you stick a 2 pole breaker into QO24L70S (which will fill all the spaces), then the assembly will have two sets of lugs, the lugs on the breaker itself, and the lugs that part of the panelboard. If that breaker is the service disconnect, then the lugs on which the service conductors land need to be guarded after the connection is made. Functionally, the service conductors can go onto either set of lugs. But if Square D only makes a guard for the lugs on the breaker, and does not make one for the lugs on the panelboard, then the service conductors have to land on the lugs on the breaker. Which is commonly referred to as "backfeeding" the breaker.
Cheers, Wayne
True. But in this case a non-issue, as the panelboard has only two spaces.They need to update the information, as starting with the 2020 you can no longer do that.
I still see new panelboards marked with the "lighting and appliance panel board" languageThey need to update the information, as starting with the 2020 you can no longer do that.
Pff, 2008 wasn't even 20 years ago.I still see new panelboards marked with the "lighting and appliance panel board" language![]()