AC unit and motor cale sizing

Status
Not open for further replies.

mbrooke

Batteries Included
Location
United States
Occupation
Technician
If an AC or had an FLA of 18 amps under the 2005 NEC, according to table 310.16 I could use #14 NM-B or THHN in conduit? However, with 310.16 changing to 310.15 (B) (16) I am now required to use #12 if the wire is NM-B or terminals are rated 60 degrees, while I could still use #14 THHN in conduit with 75*C terminals?

Same with a motor under 2014?
 
For clarity, if I may substitute MCA for your FLA, I am in agreement with your post.
 