AC unit conduit derating and fill

Status
Not open for further replies.

mannyb

Senior Member
Location
Florida
Occupation
Electrician
The drawings call for the HV panel xfmr and lv panel for AC units be located on roof. I am trying not to run a bunch of conduit because there is around 14 RTU and 12 ACCUs I want to share conduit and run at least 2 units per conduit or should I run each unit individual. I can provide more info just trying to figure if 1 or 2 or 3 is a good idea depending.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
Won't there be penetrations at each unit? I would run a conduit for 2-3 units and run up thru the roof individually. If you run more than 3 units you probably will have to use larger wire
 