AC unit multi family

Status
Not open for further replies.

MBLES

Senior Member
I have 4 condenser 3 phase 208 40.8 RLA amps for compresser and 5.3 for fans. for multifamily. I am trying to determine the the branch circuit conductor. do i add up all the 184.4 x 125% =230A OR 4/0 WIRE
 
Last edited:

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
I have 4 condenser 3 phase 208 40.8 RLA amps for compresser and 5.3 for fans. for multifamily. I am trying to determine the the branch circuit conductor. do i add up all the 184.4 x 125% =230A OR 4/0 WIRE


Do you mean FLA--= 40.8? I believe you are trying to find the feeder size and not the branch circuit. Is that correct?
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
Take a look at this

440.33 Motor-Compressor(s) With or Without Additional
Motor Loads. Conductors supplying one or more motorcompressor(
s) with or without an additional motor load(s)
shall have an ampacity not less than the sum of each of the
following:
(1) The sum of the rated-load or branch-circuit selection
current, whichever is greater, of all motor-compressor(s)
(2) The sum of the full-load current rating of all other
motors
(3) 25 percent of the highest motor-compressor or motor full
load current in the group
 

Mouser

Member
Location
Riverside, CA.
Multifamily...

My first question is:

with your plan to run one set of conductors to ALL of the AC units, which multifamily unit get to pay for the three other families AC bill?

Normally we run a circuit from each units panel to each condenser unit and the conductor sizes are based on the MCA on the units nameplate.

But then again it's Friday and I could have misinterpreted your OP.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
Multifamily...

My first question is:

with your plan to run one set of conductors to ALL of the AC units, which multifamily unit get to pay for the three other families AC bill?

Normally we run a circuit from each units panel to each condenser unit and the conductor sizes are based on the MCA on the units nameplate.

But then again it's Friday and I could have misinterpreted your OP.

I was confused also. If he wants a branch circuit then why would he be adding all 4 together. The branch circuit for each would usually be marked on the unit as MCA or minimum circuit ampacity
 

MBLES

Senior Member
Do you mean FLA--= 40.8? I believe you are trying to find the feeder size and not the branch circuit. Is that correct?

Sorry I was thinking of another job with a similar problem. I found answer upon reading other similar post.


Yes Sir The Feeder Size is what I am looking for Its basically a chiller feeder that has 4 condenser units FLA 40,8 a and 5.3 fan motor.. Name plate MCA 194.6 and MOCP 225a. IS the feeder sized by the 194.6 on name plate? do i add the 125% to get feeder size? or just use whats on name plate MCA 194.6amps to find size wire needed. The name plate also limits the OCPD to MOCP 225. The job is an all bills paid apartments.
 

jumper

Senior Member
Sorry I was thinking of another job with a similar problem. I found answer upon reading other similar post.


Yes Sir The Feeder Size is what I am looking for Its basically a chiller feeder that has 4 condenser units FLA 40,8 a and 5.3 fan motor.. Name plate MCA 194.6 and MOCP 225a. IS the feeder sized by the 194.6 on name plate? do i add the 125% to get feeder size? or just use whats on name plate MCA 194.6amps to find size wire needed. The name plate also limits the OCPD to MOCP 225. The job is an all bills paid apartments.

You just follow the nameplate. No additional math needed.

3/0 CU or 250 AL and a 225A breaker.
 

kwired

Electron manager
Location
NE Nebraska
Safety switch would be more common IME.
225 amp breaker might be less $$ than a 400 amp safety switch.

200 amp non fused safety switch might be rated for the overall HP rating also even if on higher than 200 amp overcurrent device ahead of it.
 

JoeStillman

Senior Member
Location
West Chester, PA
Me just follow prints/specs....

Me just draw those prints/specs.

I still always call for a fused disconnect for all refrigeration equipment. There are two good reasons; even though your mechanical department might have specified a unit listed for use with a fuse or HACR breaker, the successful bidder might win the job with a substitution that is rated with fuse only. Secondly, if the equipment branch circuit is short, you might exceed the (typical) 5 kAIC rating. With a fusible switch on-site, you've got a fighting chance of getting a current-limiting fuse that protects the under-duty equipment.

Anyone else here insist on fusible disconnects for all refrigeration equipment?
 