Happy hump day to all pros on this site. I have a question about a AC unit installed in a four year old house that I am in the process of buying.
The house has a 3 ton unit, air handler in the attic, gas powered heat.
The specs on the name sticker is as follows : compressor-19.9 RLA. Fan motor 1/4hp 1.4 FLA. Minimum circuit amps 26.2 amps. Maximum fuse 40 amps. Maximum circuit breaker 40 amps.
From the panel to the unit is about 10 feet. The panel has a 40 amp breaker fed by #10 wires to a pull-out disconnect rated at 30 amps. #10 wires from the disconnect to the unit. The home inspector says everything is fine except for the disconnect which he says should be rated more than 30 amps. Home owner's inspector disagrees and says 30 amp is fine. Who is correct?
Also air handler is protected by 15 amp circuit.
Any help would be greatly appreciated.
The house has a 3 ton unit, air handler in the attic, gas powered heat.
The specs on the name sticker is as follows : compressor-19.9 RLA. Fan motor 1/4hp 1.4 FLA. Minimum circuit amps 26.2 amps. Maximum fuse 40 amps. Maximum circuit breaker 40 amps.
From the panel to the unit is about 10 feet. The panel has a 40 amp breaker fed by #10 wires to a pull-out disconnect rated at 30 amps. #10 wires from the disconnect to the unit. The home inspector says everything is fine except for the disconnect which he says should be rated more than 30 amps. Home owner's inspector disagrees and says 30 amp is fine. Who is correct?
Also air handler is protected by 15 amp circuit.