I am going with no.
If it would stay ungrounded that would be another matter but between faults and capacitance coupling it would not protect humans from shocks.
The ungrounded systems in hospitals are kept small and with constant monitoring to endpsure they stay isolated
If we used a ungrounded ac system when we started using ac voltage would it be safer now ?
If we used a ungrounded ac system when we started using ac voltage would it be safer now ?
Speaking as someone who has received a very strong shock on an ungrounded system, I can absolutely attest to this hazard. I might even argue that the potential for shock is more severe as phase voltage floats compared to earth. In my case it was about 400 volts.We all deal with capacitance coupling but I never heard of it being capable of a fatal sock. can you give me a example of this in a home and a biasness and industrial please ?
So, not just one ground fault detector per secondary, but a "super duper directional GF detector" that could detect the low capacitive current from an accidental ground, or else a lower resistance deliberate ground current generator/detector such as the indicator lamps used for commercial ground detection, but somehow isolated from everyone else on the same secondary.In a small, low voltage system like a house it might offer limited protection, but we would need to install sensing circuits at every main or the ungrounded status would never be maintained.
In a small, low voltage system like a house it might offer limited protection, but we would need to install sensing circuits at every main or the ungrounded status would never be maintained.
Ungrounded where?
Are you saying:
The utility distribution is ungrounded?
The customer side of the service transformer is ungrounded?
Or maybe both?
ice
Alright - both.Both.
With typical 120/240 or even 208/120 systems what we currently have is already referenced to ground at the neutral point - so the upper limit of the capacitively coupled voltages will be limited to 120 volts. You can increase this to 277 for systems that operate at that voltage to neutral.We all deal with capacitance coupling but I never heard of it being capable of a fatal sock. can you give me a example of this in a home and a biasness and industrial please ?
Really suggest to limit the discussion to either Distribution MV/HV, or comsumer side MV, or industrial LV (480V), or consumer 240/208V. Otherwise the topic is way too broad. The issues are not the same."Lightning strikes on ungrounded distribution lines have a much higher potential (pun intended) for destroying equipment than strikes on grounded distribution lines."
Why doesn't anyone combine the advantages of an ungrounded system with the improved lightning safety of a grounded one by doing the grounding through a gas discharge tube or other lightning arrestor, something normally open but which will snub an overvoltage to ground?
"Lightning strikes on ungrounded distribution lines have a much higher potential (pun intended) for destroying equipment than strikes on grounded distribution lines."
Why doesn't anyone combine the advantages of an ungrounded system with the improved lightning safety of a grounded one by doing the grounding through a gas discharge tube or other lightning arrestor, something normally open but which will snub an overvoltage to ground?
I like your idea. I would say that the same system with conventional wiring methods would be a functional and safer, using MI cable is just gilding the Lilly.The OP said both distribution and Consumer side of transformer, but most all of the posts appear to be about consumer. So, addressing consumer side, I don't know - probably money.
However, if we are addressing ripping out the entire US non-utility electrical systems and replacing with a systems that stress personnel safety, structural safety (fire), and continuity of service - Maybe investigate:
All distribution from the substation to the consumer transformers are underground - all pad mound transformers. I'll leave the distribution grounded/un-grounded issues alone.
Do not connect the consumer side neutral to the distribution side neutral.
Consumer side (480, 208)is all 3phase, HRG, underground to Consumer first disconnect. All loads are line to line - no line to neutral loads available.
Set the ground detectors to shut off the power if gf is detected
Wire buildings in MI cable. Or if the money bleed gets to where the customers are dying out, go with MC-HL - that will just leave them somewhat anemic.
So, my answer is: Neither grounded nor un-grounded - rather HRG
Mind you , these are just random thoughts, indiscriminately leaking out. I'm certainly not telling anyone this is the answer.
ice
I understand how HRG works, never been around such a system though.The OP said both distribution and Consumer side of transformer, but most all of the posts appear to be about consumer. So, addressing consumer side, I don't know - probably money.
However, if we are addressing ripping out the entire US non-utility electrical systems and replacing with a systems that stress personnel safety, structural safety (fire), and continuity of service - Maybe investigate:
All distribution from the substation to the consumer transformers are underground - all pad mound transformers. I'll leave the distribution grounded/un-grounded issues alone.
Do not connect the consumer side neutral to the distribution side neutral.
Consumer side (480, 208)is all 3phase, HRG, underground to Consumer first disconnect. All loads are line to line - no line to neutral loads available.
Set the ground detectors to shut off the power if gf is detected
Wire buildings in MI cable. Or if the money bleed gets to where the customers are dying out, go with MC-HL - that will just leave them somewhat anemic.
So, my answer is: Neither grounded nor un-grounded - rather HRG
Mind you , these are just random thoughts, indiscriminately leaking out. I'm certainly not telling anyone this is the answer.
ice
... I have also heard from people that have been around them that there never seems to be any concern when a ground fault is indicated, which leaves you wonder why they have the HRG in the first place if they are going to ignore faults that are indicated, a second fault is going to present problems, maybe nothing severe if you are lucky for it to be on same phase as the first fault, but there is still potential for objectionable current in unpredictable paths when that happens.