KY Solar
- Owensboro, Kentucky, USA
My first post on MH.
We are wrapping up a 30kW solar array that is based on (100) ABB 300W micro-inverters :slaphead:.
The main feed wire is MCM250 Cu and travels a distance of 365'. Nominal load is 120A.
The wire feeding each trunk cable is 12-3 UF-B. Average length is 100'. Nominal load is 7.5A.
Nominal "solar off" voltage is 250 at the meter can.
We anticipated some voltage rise but the solar array is driving up voltage at the meter can by about 5 volts to 255.
The underground wiring adds another 5 volts to 260.
Although the micros are rated to 264 volts, we are seeing some instability and inverters dropping out during mid day at 260 volts.
We have opened up the voltage parameters within the micro-inverters to the max allowed (132 / 264 volts).
Two options:
1.) Get the local utility to install a new 25kVA transformer with taps, dropping all secondary voltage on site by 2.5%.
2.) Install Buck Boost transformers on the main AC feed wires, dropping the voltage to the solar array by 5%.
Questions:
Thanks!
Two options:
Questions:
- What would you do to reduce the voltage as seen at the micro-inverters?
- The micro-inverters depend on a well balanced Neutral for proper function. Do we need two (2) buck boost transformers to maintain a good Neutral?
- Who makes the best quality outdoor rated Buck Boost transformers? (probably about 2kVA).
Thanks!