Re: AC vs. MC vs. MC Lite
AC cable (Steel Jacket for grounding)
I used to install this a lot, not any now except for hospital grade AC (This is AC cable with insulated ground) We use this for IG circuits sometimes.
I think it is out of favor in my area due to lack of a copper grounding conductor, but it is a tough and durable product, heavy to work with.
MC cable (Steel Jacket NOT for grounding)
What we install some of the time, it is a tough and durable product, heavy to work with.
MC lite (Aluminum Jacket NOT for grounding)
What we install most of the time, one guy can handle 1000' spools of 12/2 and 12/3, and the light weight allows us to pull a few long home runs at a time, not so easy with steel.
It strips easily with dikes (kink, cut, and straighten) or rotosplits just a couple of turns.
Not so durable, if it is not supported properly or if you are to rough with it on the install it will kink. Limited use of connectors, can not be used with the set screw type of connectors.
Fire Alarm MC is always steel on the jobs I have worked, and gets expensive, they tell me 16/2 TW/SP F/A MC is 4 times the price of 12/2 MC
Twisted shielded also takes time to make entry into connectors with out shorting the shield to ground.
MC for feeders, the largest size I have used is 4/0-4 this is hard to install if you go at it like it is a branch circuit, but with some planning it can go in very quickly, a few pulleys, a good rope and enough hands you quickly run a 200 amp 3P 5W feeder complete.
Like most electricians we use Antishorts on MC even though not a code requirement.
We always order our spools reverse wound, this used to be harder to get but now no problem. There is a tremendous difference in ease of pulling armored cable depending on which way it comes off the spool, if you look closely at it you can see why.
Steel MC is what I would specify, if it was up to me.
Hope this helpful and not to rambling.