I found this article and have some concerns about it, but I'd like to hear from this community of professionals as to your opinions. It's about a 5 minute read:
 

charlie b

Moderator
Staff member
Location
Lockport, IL
Occupation
Semi-Retired Electrical Engineer
I didn't see anything that stood out as being inaccurate or confusing. What are your concerns?
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
I found this article and have some concerns about it, but I'd like to hear from this community of professionals as to your opinions. It's about a 5 minute read:

Are you concerned about #12 wire and then using a 30 amp breaker? This is compliant as the overload in the motor will handle any current overload. The breaker, in this case, is only for protection from ground faults and short circuits, not overloads.
 

Crash117

Senior Member
Location
Nevada
Occupation
C-2 electrical contractor/owner operator
All the information supplied in the article seems accurate at first glance
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
I found this article and have some concerns about it, but I'd like to hear from this community of professionals as to your opinions. It's about a 5 minute read:
What are your concerns? The only thing that it failed to mention is that you could actually use #14 AWG conductors with a 30 amp OCPD if not using a 60° C wiring method like NM cable.
 

Brian918

Member
Location
Tulsa
Occupation
Estimator
Are you concerned about #12 wire and then using a 30 amp breaker? This is compliant as the overload in the motor will handle any current overload. The breaker, in this case, is only for protection from ground faults and short circuits, not overloads.
That's what stood out to me - I misunderstood the line about 'Normally this is too big to protect the 12 AWG wire, but the wire is protected by the air conditioner.' Thank you for the information!
 

Brian918

Member
Location
Tulsa
Occupation
Estimator
Thank you all for your insight here. I misunderstood what the author was trying to convey but you all cleared it up. Thanks again!
 