I'm looking @ my copy of Mike Holt's "Electrical Formulas with Sample Calculations" book. And one of the examples has me puzzled.
Page 78 for those who have the book.
Here is how it reads.
Q. An air conditioner nameplate indicates the minimum circuit ampacity of 23A and a maximum fuse size of 40A. What is the minimum size branch-circuit conductor and the maximum size overcurrent protection device 75 degree C.
A. 12awg, 40A fuse
Conductor: The conductors must be sized based on the 60 degree C column of table 310.16 and 12 awg rated 25A.
Overcurrent protection:The overcurrent protection device must not be greater than a 40A fuse, either one-time or dual element.
My question is, if the terminals are rated for 75 degrees C why do we need to use the 60 degree table. In this particular example it wouldn't matter #12 is good for 25A in both the 75 & 60 degree columns.
Where does the 60 degree requirement come from?