I have to do an estimate for a AC split system with blower in computer room and condenser on rooftop.. both 460V.

Both units have a combined WSA of 46.2A and a FLA of 38.4 with OPD of 21A and 30A.

Is there anyway I can run #8 to a point above ceiling and feed blower motor and then run #10 out to condenser?

Having OPD above ceiling for condenser is what has me stumped..
 

danickstr

Senior Member
Even if you could gutter tap it, it seems like more work in the ceiling than running one pipe of 2 sets of wires and just j-boxing them at a split point.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
Yes.. I am trying to find some way of getting past 110.26 legally.. sometimes there are exceptions that only a select few know about.
I am not one of those select few. I know someone who got hit on that 20 years ago-- :). I was feeding a furnace under the house and an outdoor a/c unit and it was too hard to get 2 feeds so... I actually didn't think about 110.26
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
If you can't get 2 circuits then pull the #8 to a JB and use #8 to both the a/c and the blower. Use fused or breaker disconnects at the unit.
 

B4T

Senior Member
If you can't get 2 circuits then pull the #8 to a JB and use #8 to both the a/c and the blower. Use fused or breaker disconnects at the unit.

I can get two circuits, but I am wiring this up using MC and space for running wires into the panel is tight.

There is a 14" space below panel I have to core bit through the concrete floor, so I was trying to keep the hole small as possible.
 