The ac company is telling me 4 ton condenser 16 seer, 4 ton 5kw air handler. They can't give me nameplate due to "not knowing what unit they will use at time of install". I have never sized the wire before using tonnage and kw just always was given mca and over current protection. Can someone shed some light on how to use tonnage/kw to determine mca and ocpd
 
Welcome to the forum.

You really need the MCA/MOC numbers.

Otherwise, I'd run #10 cu to the air handler and #8 cu to the compressor.
 
You always look up any manufacturers specifications to get you close. For example I looked up a Carrier 16 SEER, 4 ton unit and it had these specs: