Acceptable form overcurrent protection

Status
Not open for further replies.

hhsting

Senior Member
Location
Glen bunie, md, us
Occupation
Junior plan reviewer
I have EV chargers cabinet which converts AC to DC stand alone remote from EV chargers

The dc cable provided has ampacity of 500A and their is no fuse or breaker provided.


The cabinet manufacturer instruction states that the cabinet have CTs which detect if more than 500A of current is passed thru DC conductors it would shut down the cabinet.

I cannot find this in NEC 2017 as acceptable form of overcurrent protection

So my questions:

1. what forms of overcurrent protection are acceptable fuse, breaker etc? Is this in NEC 2017 some where?

2. Would something above be acceptable form of overcurrent protection or not?
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
Sounds like it's covered by the Original Equipment Manufacturer.
I would not concern myself with it other than to check for NRTL listing if that's required in your jurisdiction.
 

hhsting

Senior Member
Location
Glen bunie, md, us
Occupation
Junior plan reviewer
I fail to see how this is not covered by NEC???

There are two separate pieces of equipment connected together by 60 feet of cable in between. The cable is provided by contractor Not by equipment manufacturer
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
Not uncommon for an "assembly" to consist of more that 1 piece of equipment under one listing.
Interconnecting cables installed per 110.3b
 

hhsting

Senior Member
Location
Glen bunie, md, us
Occupation
Junior plan reviewer
Could be or maybe not. However is their anything in NEC 2017 that says acceptable forms of overcurrent protection? Such as breaker fuse etc
 

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
I have EV chargers cabinet which converts AC to DC stand alone remote from EV chargers

The dc cable provided has ampacity of 500A and their is no fuse or breaker provided.


The cabinet manufacturer instruction states that the cabinet have CTs which detect if more than 500A of current is passed thru DC conductors it would shut down the cabinet.

I cannot find this in NEC 2017 as acceptable form of overcurrent protection

So my questions:

1. what forms of overcurrent protection are acceptable fuse, breaker etc? Is this in NEC 2017 some where?

2. Would something above be acceptable form of overcurrent protection or not?
Is it listed
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Ok but exactly which section in it?
no idea, but I though you knew how to read....however there is no reason to believe that any additional OCPD is required based on the LIMITED information that you have provided.
 
Last edited by a moderator: