Acceptable to use 3p 3w 600v Safety Switch for 1p Load?

Status
Not open for further replies.

cmesker

Member
Location
Columbus
Occupation
Construction Manager
Is it acceptable to utilize a 3p 3w 600v safety switch for a 1p load? Ie taking 1 hot and 1 neutral and disconnecting 1 hot (using 1 of the 3 poles in the disconnect) and leaving the neutral running thru the disconnect. This would leave 2 of the 3 poles within the disconnect empty. Is this allowed?
 
Welcome to the forum.

Sounds like an expensive option, though. Would a simple toggle switch work, perhaps HP rated?
 
Yes BUT you need to even the wear. Wire it up either with 3 poles in parallel or looping poles in series.
 
You can use two of the poles for the neutral and ungrounded conductor in the switch. See 404.2(B) Exception.
 
Yes BUT you need to even the wear. Wire it up either with 3 poles in parallel or looping poles in series.

Required, or simply a suggestion to increase switch life? Or just a joke?

I have specifically seen a manufacturer requirement to use all 3 poles when switching two wire DC, one condictor looped through 2 poles, the other conductor through the third.

Jon
 