The modular nature of Wifi modules lends itself to multiple installation locations. What rating does a WiFI comm cable and Power 10vdc barrel cable insulation need to be rated at? Is there a NEC code restriction to securely mounting WiFi modules inside panel access doors with plenty of space via a cable leash. Behind the inverter access door are typical seizure lugs from DC to AC. All of these wire conductors typically 12ga to 8ga, THHN insulation are rated at 600V.
Do very small managed conductor cables, 24ga and Cat 5 or 6 sheathing and insulation also need to be rated at 600v, just because it is in the general vicinity of the heavier conductors and termination enclosure area. I can only find 300v rated sheathing. The actual comm ports on the inverter are in fact in the cable termination area. Also placing the wifi monitoring device inside the inverter panel would remove the external enclosure cost, be weather resistent and make the installation much cleaner and cheaper. With the initial testing we've done, EMF is a non-issue.
Will this pass code? I?ve not found anything in the code specific to this.
Do very small managed conductor cables, 24ga and Cat 5 or 6 sheathing and insulation also need to be rated at 600v, just because it is in the general vicinity of the heavier conductors and termination enclosure area. I can only find 300v rated sheathing. The actual comm ports on the inverter are in fact in the cable termination area. Also placing the wifi monitoring device inside the inverter panel would remove the external enclosure cost, be weather resistent and make the installation much cleaner and cheaper. With the initial testing we've done, EMF is a non-issue.
Will this pass code? I?ve not found anything in the code specific to this.