Access to Terminal Lugs
Access to Terminal Lugs
Yes, that is correct. If they are "Electrical", then they are covered under 110.26(A)(1). IF they are non-electrical, they are covered under the last sentence of 110.26(A)(1)(a). the 2002 NEC hand book uses an example of a UPS that has filters in the back.
This is the 2002 NEC Hand book comment after 110.26(A)(1)(a).
"The intent of this section is to point out that work space is required only from the side(s) of the enclosure that requires access. The general rule still applies: Equipment that requires front, rear, or side access for electrical activities described in 110.26(A) must meet the requirements of the table 110.26(A)(1). In many cases, equipment of "dead front" assemblies requires only front access. For equipment taht required rear access for non-electrical activity, however, a reduced working space of at least 762mm (30 in.) mus be provided."
So, if the back of the gear has to be accessed while energized, table 110.26(A)(1) applies requiring 36, 42, or 48" of space depending on voltage. If, however, the gear is designed for rear access for non-energized or non-electrical work (changing filters, accessing lugs), then at least 30" of space are required.
Based on the above paragraph, would you not agree that a minimum of 30" of space for rear access should be provided to work on the lugs?