Access to large equipment.
I work for a general contractor on a project to design/construct a dining facility for the government. I am involved in an interesting question regarding access/egress for large equipment. One party says the electric code requires two doors in the electric room in order to satisfy code requirements for large equipment. A different party makes the following argument:
Paragraph 110.26(C)(2) of the NEC states:
"(C) Entrance to Working Space
(1) Minimum Required. At least one entrance of sufficient area shall be provided to give access to and egress from working space about electrical equipment.
(2) Large Equipment. For equipment rated 1,200 amperes or more and over 1.8 m (6 ft.) wide that contains overcurrent devices, switching devices, or control devices, there shall be one entrance to the required working space not less than 610 mm (24 in.) wide and 2.0 m (6? ft.) high at each end of the working space."
It is important to understand that the code is referring to ?working space? as defined by Paragraph 110.26(A), and not a ?room?. The working space for any piece of electrical equipment in Electrical Room 224 extends 36? (for 208/120V) or 42" (for 480/277V) from the face of the equipment in order to comply with Condition 2 of Table 110.26(A)(1). The attached sketch shows the working space of Main Switchboard ?MSB? highlighted in yellow. [Although only ?MSB? is shown highlighted, this procedure and reasoning also works for every other piece of electrical equipment in this room.] As you can see, the ?working space? about each piece of electrical equipment has entrances and exits at each end.
Being a new poster, I could not post the sketch that would clarify the above description. The electric room is 20' x 20' with one double door centered on one wall. The other walls have equipment. There is a transformer in the center of the room with at least 6' clearance on all sides.
I would be interested in how others interpret this problem.
I work for a general contractor on a project to design/construct a dining facility for the government. I am involved in an interesting question regarding access/egress for large equipment. One party says the electric code requires two doors in the electric room in order to satisfy code requirements for large equipment. A different party makes the following argument:
Paragraph 110.26(C)(2) of the NEC states:
"(C) Entrance to Working Space
(1) Minimum Required. At least one entrance of sufficient area shall be provided to give access to and egress from working space about electrical equipment.
(2) Large Equipment. For equipment rated 1,200 amperes or more and over 1.8 m (6 ft.) wide that contains overcurrent devices, switching devices, or control devices, there shall be one entrance to the required working space not less than 610 mm (24 in.) wide and 2.0 m (6? ft.) high at each end of the working space."
It is important to understand that the code is referring to ?working space? as defined by Paragraph 110.26(A), and not a ?room?. The working space for any piece of electrical equipment in Electrical Room 224 extends 36? (for 208/120V) or 42" (for 480/277V) from the face of the equipment in order to comply with Condition 2 of Table 110.26(A)(1). The attached sketch shows the working space of Main Switchboard ?MSB? highlighted in yellow. [Although only ?MSB? is shown highlighted, this procedure and reasoning also works for every other piece of electrical equipment in this room.] As you can see, the ?working space? about each piece of electrical equipment has entrances and exits at each end.
Being a new poster, I could not post the sketch that would clarify the above description. The electric room is 20' x 20' with one double door centered on one wall. The other walls have equipment. There is a transformer in the center of the room with at least 6' clearance on all sides.
I would be interested in how others interpret this problem.