SoFloBuc
Member
- Location
- South Florida
- Occupation
- Manager for Electrical. plumbing and AC shop
Multi story condominium, total gut and rewire project. Kitchen being totally overhauled including the panel location, a large junction box was installed in the wall below where the panel was and set in a location where the cover will be assessable in the lower cabinets back wall. Inspector is saying that we cant have it there, the face of the box will stick out past the cabinet back wall (314.20 is covered) and "rendered accessible without removing any part of the building or structure" per 314.29 when the cabinet doors are open. Box sizing was also considered. This isn't the most optimal location to work but lets face it there are a lot of electrical equipment installs where we have to be contortionists to access splices or terminals. Do you see a reason i shouldn't argue this? (The permit was pulled under the 2017 code cycle)